F013 Motor overload fault in Schneider drive
Cause : Motor overload comes when the connected motor is drawing excessive current, potentially damaging the motor and drive. This fault is triggered by excessive motor current.
"F013" fault in Schneider drive indicate an "Motor overload" condition. This means the connected motor is drawing excessive current, which can lead to overheating and potential damage.
  1. Check Motor Load: Ensure the motor is not overloaded and operating within its rated capacity.
  2. Verify Motor Parameters: Confirm that the motor parameters (power, current, voltage, etc.) are correctly entered in the drive.
  3. Inspect Motor Thermal Protection: Check the motor's thermal protection device for proper operation.
  4. Review Drive Configuration: Verify the drive's current limit, motor protection, and other relevant parameters.
