F015 3 Output phases loss fault in Schneider drive
Cause : 3 Output phases loss comes when all three phases of the motor are disconnected or faulty. The cause of this fault is motor not connected or motor power too low, below 6% of the rated drive current.
"F015" fault in Schneider drive indicate "Output phases loss" This means the drive is completely unable to supply power to the motor.
  1. Check Motor Connections: Ensure all connections between the drive and motor are tight and secure.
  2. Inspect Motor Cable: Examine the motor cable for any visible damage, cuts, or signs of overheating.
  3. Verify Drive Output: If possible, check the voltage output of each phase from the drive to confirm if one phase is missing.
  4. Test Contactor or Relay: If using a contactor or relay, verify its operation.