LFF2 AI2 4-20mA loss fault in Schneider drive
Cause : AI2 4-20 mA loss comes when the analog input current is below the minimum threshold value. This means loss of the 4-20 mA on analog input AI1.
An "LFF2" fault in a Schneider drive indicates "AI2 4-20 mA loss" This means the analog input (AI2), which is configured to receive a 4-20 mA signal, has lost its signal. This fault can be due to issues with the sensor, wiring, or configuration settings.
Steps to Address an LFF2 AI2 4-20 mA Loss Fault:
  1. Immediate Actions:
    • Stop Operation: If the drive is running, stop it to prevent any potential damage or unsafe conditions.
    • Reset Error: Attempt to reset the error using the drive’s control panel. This may clear temporary issues.
  2. Check the Sensor:
    • Sensor Operation: Ensure that the sensor providing the 4-20 mA signal is operating correctly.
    • Power Supply: Verify that the sensor has the correct power supply and is turned on.
  3. Inspect Wiring and Connections:
    • Wiring Continuity: Check the wiring between the sensor and the drive’s AI2 input for continuity. Use a multimeter to verify that there are no breaks or shorts in the wiring.
    • Connections: Ensure that all connections are secure and free from corrosion or damage. Tighten any loose connections.
  4. Measure the Signal:
    • Multimeter Measurement: Use a multimeter to measure the current at the AI2 input terminal on the drive. Ensure that the signal is within the 4-20 mA range.
    • Signal Consistency: Ensure the signal is stable and not fluctuating outside the 4-20 mA range.
  5. Check Configuration Settings:
    • Parameter Settings: Verify that the drive is correctly configured to accept a 4-20 mA signal on AI2. Ensure that the input is not set to another mode (e.g., 0-10 V).
    • Scaling and Filtering: Check the scaling and filtering settings for AI2 to ensure they are appropriate for your application.
  6. Inspect for Electrical Noise:
    • Noise Sources: Identify and mitigate any potential sources of electrical noise that could be affecting the 4-20 mA signal. This includes ensuring proper grounding and shielding of the sensor wiring.
    • EMI/RFI Filters: Ensure that any installed EMI/RFI filters are functioning correctly and consider adding them if none are present.