Cause : Modbus communication interruption comes when communication interruption on the Modbus port if the command and/or reference value is given by Modbus.
"SLF1" fault in Schneider drive indicate "Modbus communication interruption". This means there's an interruption in the communication between the drive and a Modbus master device (like a PLC or HMI).
Follow These Steps to Correct SLF1 Modbus communication Fault:
Inspect Communication Connections:
- Physical Inspection: Check the Modbus wiring for loose or damaged connections. Ensure that all terminals are secure.
- Cable Condition: Look for any signs of wear or damage to the communication cables.
Verify Communication Parameters:
- Configuration Check: Ensure that the Modbus parameters (baud rate, parity, stop bits) on the drive match those of the control system.
- Address Verification: Confirm that the Modbus address set in the drive matches the expected address from the control system.
Run Diagnostics:
- Diagnostic Tools: Use Schneider Electric diagnostic tools to check the status of the drive and communication settings.
- Error Logs: Review error logs for any additional information or related communication faults.
Test with a Known Good Setup:
- Substitution Test: If possible, connect the drive to a known good control system to verify communication.
Check for Interference:
- Environmental Factors: Ensure that there are no sources of electrical interference (motors, transformers) affecting the Modbus communication.