Forum

Share:
Notifications
Clear all

CBF Circuit breaker error fault in Schneider ATV610 drive

1 Posts
1 Users
0 Reactions
114 Views
Posts: 18023
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Circuit breaker error comes when the DC bus voltage level is incorrect compared to the circuit breaker logic control (start or stop pulse) after the configured timeout. This means the drive has detected an issue with the circuit breaker that protects the motor connected to it.

A CBF fault in Schneider ATV610 drive indicates a Circuit Breaker fault. This means the drive has detected an issue with the circuit breaker connected to the motor.

  1. Verify the circuit breaker logic control (pulse time for start and stop).
  2. Verify the mechanical state of the circuit breaker.
  3. Verify the measured values of [DC bus voltage] VBUS and [Mains Voltage] ULN parameters.
Share: