1,677
Jul 18, 2024 5:03 am
Cause : Output phases loss comes when all three phases of the motor are disconnected or faulty. The cause of this fault is motor not connected or motor power too low, below 6% of the rated drive current.
"F015" fault in Schneider ATV310 drive indicate "Output phases loss" condition. This means the drive is completely unable to supply power to the motor.
- Check Motor Connections: Ensure all connections between the drive and motor are tight and secure.
- Inspect Motor Cable: Examine the motor cable for any visible damage, cuts, or signs of overheating.
- Verify Drive Output: If possible, check the voltage output of each phase from the drive to confirm if one phase is missing.
- Test Contactor or Relay: If using a contactor or relay, verify its operation.