F017 Input phase loss fault in Schneider ATV310 drive

1 Posts
1 Users
0 Reactions
152 Views
Posts: 18023
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Input phase loss comes when one of the three input phases supplying power to the drive is missing or has insufficient voltage. The drive is not connected to a three-phase power supply.

"F017" fault in Schneider ATV310 drive indicate "Input phase loss" condition. This means there is a problem with the incoming power supply, such as a phase imbalance or voltage drop.

Follow these steps to correct the fault:

  1. Check Power Supply: Verify that the drive is connected to a three-phase power supply and that all phases are present.
  2. Inspect Fuses: Check the input fuses for the drive and replace any that are blown.
  3. Measure Input Voltage: Use a multimeter to measure the voltage on all three input phases to check for imbalances or low voltage.