SLF1 Modbus communication fault in Schneider ATV610 drive
Cause : Modbus communication interruption comes when communication interruption on the Modbus port if the command and/or reference value is given by Modbus.
"SLF1" fault in Schneider ATV610 drive indicate Modbus communication interruption. This means there's an interruption in the communication between the drive and a Modbus master device (like a PLC or HMI).
Follow These Steps to Correct SLF1 Modbus communication Fault:
  1. Inspect Communication Connections:
    • Physical Inspection: Check the Modbus wiring for loose or damaged connections. Ensure that all terminals are secure.
    • Cable Condition: Look for any signs of wear or damage to the communication cables.
  2. Verify Communication Parameters:
    • Configuration Check: Ensure that the Modbus parameters (baud rate, parity, stop bits) on the drive match those of the control system.
    • Address Verification: Confirm that the Modbus address set in the drive matches the expected address from the control system.
  3. Run Diagnostics:
    • Diagnostic Tools: Use Schneider Electric diagnostic tools to check the status of the drive and communication settings.
    • Error Logs: Review error logs for any additional information or related communication faults.
  4. Test with a Known Good Setup:
    • Substitution Test: If possible, connect the drive to a known good control system to verify communication.
  5. Check for Interference:
    • Environmental Factors: Ensure that there are no sources of electrical interference (motors, transformers) affecting the Modbus communication.