Cause : Thermal sensor error on AI5 comes when the thermal monitoring function has detected an error of the thermal sensor connected to the analog input AI5.
"T5CF" fault in Schneider ATV610 drive indicate Thermal sensor error on AI5. This means a "short circuit" or "open circuit" condition on terminal AI5.
- Verify the sensor and its wiring.
- Replace the sensor.
- Verify the setting of "AI5 Type" AI5T parameter.