Cause : Inverter overtemperature comes when the internal components of the drive that regulate motor speed are experiencing excessive heat.

"f0004" fault in siemens micromaster 440 indicate "Inverter overtemperature" condition. This means the temperature inside the inverter has exceeded the allowable limit. 

Troubleshooting Steps:

  1. Check Cooling and Ventilation:

    • Ensure that the drive is installed in a location with adequate ventilation and airflow.
    • Verify that cooling fans (if applicable) are operating correctly and that vents are not blocked.
  2. Measure Ambient Temperature:

    • Confirm that the ambient temperature around the drive is within the specified operating range. Refer to the drive’s documentation for the acceptable temperature range.
  3. Inspect for Overloading:

    • Check if the drive is operating beyond its rated capacity. Reduce the load if necessary and ensure that the drive is sized appropriately for the application.
  4. Clean the Drive and Environment:

    • Inspect the drive for dust or debris and clean it if needed. Ensure that the installation environment is clean and free of contaminants.
  5. Check for Proper Airflow:

    • Ensure there is enough clearance around the drive to allow for proper airflow. Avoid placing the drive in enclosed spaces without adequate ventilation.
  6. Verify Temperature Sensor:

    • If possible, check the functionality of the temperature sensors within the drive. If the sensor is faulty, it may need to be replaced.