f30005 fault in siemens drive

1 Posts
1 Users
0 Reactions
63 Views
Posts: 19848
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause: Overload I2t comes when the power unit has experienced an overload condition based on the current and the duration of the overload.

f30005 fault in siemens drive indicates a motor overload based on the I²t (current squared times time) protection model. This is a thermal model that simulates motor heating and trips to protect the motor from overheating.

Troubleshooting Steps:

  • Reduce the continuous load.
  • Check the motor and power unit rated currents.
  • Ensure the mechanical load is within the motor's and drive's specifications.
  • Confirm that the motor's rated current and power are compatible with the drive's ratings.
  • Check the motor terminal box for correct wiring according to the motor and drive manuals.