Siemens Drives
1
Posts
1
Users
0
Reactions
11
Views
Apr 28, 2025 6:17 am
Cause : Supply voltage incorrectly parameterized comes when the measured DC voltage lies outside the tolerance range after pre-charging has been completed.
f6310 siemens indicates supply voltage incorrectly parameterized. This means that the value you have set in parameter p0210 (which defines the mains/supply voltage connected to the drive) does not match the actual voltage being measured by the drive.
Troubleshooting Steps:
Follow these steps to correct f6310 siemens:
- Use a calibrated multimeter to measure the actual AC mains voltage being supplied to the drive's input terminals.
- Verify that the drive's voltage rating (indicated on its nameplate) is compatible with the actual supply voltage.
- Check the line supply voltage.
- Check the parameterized supply voltage and if required change (p0210).