A001 alarm in siemens master drive

1 Posts
1 Users
0 Reactions
350 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Calculating time comes when the calculating time utilization of the CUVC board is too high. This means the control unit is being overburdened with processing tasks.

  1. Observe r829 CalcTimeHdroom.
  2. Increase P357 Sampling Time.
  3. Reduce P340 Pulse Frequency.