Cause : Drive not synchronous comes when synchronization has been activated, the drive is not synchronous due to poor communication connection.
- Check r748 i002 and i003 = counters for CRC faults and timeout faults.
- Check the fiber-optic cable connection.
- Check P751 on the dispatcher (connector 260 must be softwired).
- Check P753 on the transceiver (corresponding SIMOLINK connector K70xx must be softwired).