Siemens SIMOVERT Master Drive
1
Posts
1
Users
0
Reactions
89
Views
Jun 28, 2024 5:30 am
Cause : Simulation active alarm comes when the DC link voltage is not equal to 0 when the simulation mode is selected (P372 = 1).
- Set P372 to 0.
- Reduce DC link voltage (disconnect the converter from the supply).