A050 alarm in siemens master drive

1 Posts
1 Users
0 Reactions
60 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Slave incorrect- At serial I/O the slaves required according to a parameterized configuration are not present (slave number or slave type): Analog inputs or outputs or digital inputs or outputs have been parameterized which are not physically present.

  1. Check parameter P693 (analog outputs), P698 (digital outputs).
  2. Check connectors K4101...K4103, K4201...K4203 (analog inputs) and binectors B4100...B4115, B4120...B4135, B4200...B4215, B4220...B4235 (digital inputs) for connecting.