Cause : fsyn > fmax comes when the measured target frequency of the external converter (or supply) is greater than the parameterized maximum frequency of the synchronizing converter.
- Check P452 n/f(max, FWD Spd)/ P453 n/f(max,REV Spd) are correct.
- Correct motor data set P578 Src MotDSet Bit0 are selected