Forum

Share:
Notifications
Clear all

A068 alarm in siemens master drive

1 Posts
1 Users
0 Reactions
70 Views
Posts: 17564
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : fsyn<>fsoll comes when the setpoint frequency of the synchronizing converter deviates too significantly from the measured target frequency of the external converter (or supply). The permissible deviation can be set in P529.

  • Adjust total setpoint (main and additional setpoints) to the target frequency displayed in visualization parameter r533.
Share: