A068 alarm in siemens master drive

1 Posts
1 Users
0 Reactions
166 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : fsyn<>fsoll comes when the setpoint frequency of the synchronizing converter deviates too significantly from the measured target frequency of the external converter (or supply). The permissible deviation can be set in P529.

  • Adjust total setpoint (main and additional setpoints) to the target frequency displayed in visualization parameter r533.