Forum

Share:
Notifications
Clear all

A131 alarm in siemens master drive

1 Posts
1 Users
0 Reactions
295 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : OFF1 missing- Control signal [OFF1] was deactivated while a traversing command was being executed. The drive is brought to a standstill via a ramp (P464 Deceleration Time). There is a subsequent pulse disable. This also valid if P443 =0 (function diagramm 310) and the ramp generator bypass (function diagramm 320) is used.

  • Check the activation of control signal [OFF1] from the user program.
Share: