Cause : Tachometer dn/dt comes when the permissible change value of the speed encoder signal P215 dn(actual, permissible) was exceeded.
- Check tachometer cables for interruptions.
- Check earthing of tachometer shield.
- The shield must be connected both at the motor and the converter side.
- The encoder cable must not be interrupted.
- The encoder cable must not be laid together with the power cables