Forum

Share:
Notifications
Clear all

F059 fault in siemens master drive

1 Posts
1 Users
0 Reactions
162 Views
Posts: 18163
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Parameter fault after factory setting/initialization comes when a fault has occurred in the initialization phase during the calculation of a parameter.

  1. The number of the inconsistent parameter is indicated in fault value r949.
  2. Correct this parameter (ALL indices) and switch voltage off and on again.
  3. Several parameters may be affected, i.e. repeat process.
Share: