Cause : Incorrect parameterization comes when that there are parameter settings within the drive that are not configured correctly or are outside of acceptable ranges. This fault can prevent the drive from operating correctly or may cause it to enter a fault state to protect itself and connected equipment.
- A parameter entered during drive setting (e.g. P107 Mot Rtd Freq, P108 Mot Rtd Speed, P340 Pulse Frequency) is not in a permissible range (depending on control type).
- Acknowledge the fault and change the corresponding parameter value. The missing parameter is indicated in r949 as a fault value.