F081 fault in siemens master drive

1 Posts
1 Users
0 Reactions
207 Views
Posts: 18163
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Option Board Heartbeat Counter comes when hartbeat-counter of the optional board is no longer being processed.

  1. Acknowledge the fault (whereby automatic reset is carried out).
  2. If the fault re-occurs, replace the board concerned (see fault value).
  3. Replace ADB.
  4. Check the connection between the subrack and the optional boards (LBA) and replace, if necessary.