Cause : Mld Time comes when the rotating measurement takes longer than programmed in a measured status due to load torque too high, load torque not uniform or ramp-function generator disabled.
- Eliminate the cause and re-start the measurement (power up the converter again).
- If it re-occurs, replace CU, or replace the unit (Compact PLUS).