Siemens SIMOVERT Master Drive
1
Posts
1
Users
0
Reactions
147
Views
Jun 27, 2024 11:42 am
Cause : Mld n(set)- This fault comes due to several reasons, check below table:
- Permissible phase sequence
- Max. frequency,
- Min. speed,
- Changeover frequency between V- and I model,
- Start of field weakening frequency,
- Frequency suppression bandwidth, it was not possible to determine a permissible frequency range for the rotating measurement.
There must be a 10% frequency range which lies above 1.1 times the changeover frequency and below 0.9 times the start of field- weakening frequency.
Possible counter-measures following as:
- Permit both phase sequences
- Increase maximum frequency
- Reduce minimum speed,
- Reduce changeover frequency between the V and I model.
- Reduce or remove the frequency suppression bandwidth.