Cause : Mld abort comes when the rotating measurement was aborted due to the inadmissible external intervention. This means the rotating measurement was aborted due to an inadmissible interruption from outside.
The fault value in r949 defines the intervention type:
- 4 Setpoint inhibit.
- 5 Changeover, setpoint channel.
- 8 Unexpected change in the converter status.
- 12 Motor data set changeover (for function selection "complete mot ID).
- 13 Changeover to the slave drive.
- 14 Motor data set changeover to data set with V/f_chara.
- 15 Controller inhibit is set.
- 16 Ramp-function generator inhibited.
- 17 "Tacho test" selected for closed-loop frequency control Remove fault.