Cause : GRND UCE comes when the ground fault test, the UCE monitoring has responded in a phase in which no valve has been triggered.
- Check valves in the power section for short-circuit, and on converters with fiber-optic gating.
- Check the gating unit wiring and the UCE checkbacks for correct assignment.
- R376 can be interrogated to indicate which UCE monitoring has responded.