F107 fault in siemens master drive

1 Posts
1 Users
0 Reactions
168 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : MLd = 0 comes when a fault has occurred during the test pulse measurement. This means during the test pulse measurement a fault occured.

  1. Check that all three motor feeder cables and motor windings are not interrupted.
  2. Check the connections between the CT and electronics.
  3. Check that the correct rating plate data have been entered for the motor data set valid during the measurement.