Siemens SIMOVERT Master Drive
1
Posts
1
Users
0
Reactions
168
Views
Jun 27, 2024 12:03 pm
Cause : MLd = 0 comes when a fault has occurred during the test pulse measurement. This means during the test pulse measurement a fault occured.
- Check that all three motor feeder cables and motor windings are not interrupted.
- Check the connections between the CT and electronics.
- Check that the correct rating plate data have been entered for the motor data set valid during the measurement.