Cause : Mld di/dt- During test pulse measurement, the current has increased significantly faster than was expected. Thus for the 1st test pulse, an overcurrent condition occurred within the first half of the minimum switch-on time.
- There may be a short-circuit between two converter outputs.
- The motor rating plate data have not been correctly parameterized.
- The motor leakage is too low.