Cause : MId OFF comes when the converter has automatically stopped the automatic measurement due to the time limit up to power-up having been exceeded or due to an OFF command during the measurement, and has reset the function selection in P115.
- Re-start with P115 function selection = 2 "Motor identification at standstill".
- The ON command must be given within 20 sec. after the alarm message A078 = standstill measurement has appeared.
- Cancel the OFF command and re-start measurement.