Cause : Buffer memory: 70% fill level reached or exceeded - comes when the non-volatile buffer memory for parameter changes is filled to at least 70%. This can also occur if the buffer memory is active (p0014 = 1) and parameters are continually changed via a fieldbus system.
If required, de-activate and clear the buffer memory (p0014 = 0).
If required, clear the buffer memory (p0014 = 2).
In the following cases, the entries in the buffer memory are transferred into the ROM and then the buffer memory is cleared:
- p0971 = 1
- power down/power up the Control Unit See also: p0014 (Buffer memory mode)