Cause : Parameter backup and device incompatible - comes when the parameter backup on the memory card and the drive unit do not match. The module boots with the factory settings.
- insert a memory card with compatible parameter backup and carry out a POWER ON.
- insert a memory card without parameter backup and carry out a POWER ON.
- If required, withdraw the memory card and carry out POWER ON.
- save the parameters (p0971 = 1)