Cause : SI P1- Deviating PROFIsafe configuration comes when he configuration of a PROFIsafe telegram in the higher-level control (F-PLC) does not match the parameterization in the drive.
Note: This message does not result in a safety stop response.
The following generally applies:
- check and, if necessary, correct the PROFIsafe configuration in the higher-level control.
Re alarm value = 1:
- remove the PROFIsafe configuring in the higher-level F control or enable PROFIsafe in the drive.
Re alarm value = 2:
- configure the PROFIsafe telegram to match the parameterization in the higher-level F-control.