A01697 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
900 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Motion monitoring functions must be tested comes when thee time set in p9559 for the forced checking procedure of the safety motion monitoring functions has been exceeded. A new test is required.
After next selecting the forced checking procedure parameterized in p9705, the message is withdrawn and the monitoring time is reset.

- This message does not result in a safety stop response.
- As the shutdown paths are not automatically checked during booting, an alarm is always issued once booting is complete.
- The test must be performed within a defined, maximum time interval (p9559, maximum of 9000 hours) in order to comply with the requirements as laid down in the standards for timely fault detection and the conditions to calculate the failure rates of safety functions (PFH value).

Operation beyond this maximum time period is permissible if it can be ensured that the forced checking procedure is performed before persons enter the hazardous area and who are depending on the safety functions correctly functioning. See also: p9559 (SI Motion forced checking procedure timer (processor 1)), p9705 (SIMotion: Test stop signal source)

Carry out the forced checking procedure of the safety motion monitoring functions.
The signal source for initiation is parameterized in binector input p9705.
See also: p9705 (SI Motion: Test stop signal source)