A07416 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
131 Views
Posts: 18018
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Flux controller configuration comes when The configuration of the flux control (p1401) is contradictory.
Alarm value (r2124, interpret hexadecimal): ccbbaaaa hex aaaa = Parameter bb = Index cc = fault cause

1: Quick magnetizing (p1401.6) for soft starting (p1401.0).
2: Quick magnetizing for flux build-up control (p1401.2).
3: Quick magnetizing (p1401.6) for Rs identification after restart (p0621 = 2).

Re fault cause = 1:
- Shut down soft start (p1401.0 = 0).
- Shut down quick magnetizing (p1401.6 = 0).

Re fault cause = 2:
- De-energize flux build-up control (p1401.2 = 0).
- Shut down quick magnetizing (p1401.6 = 0).

Re fault cause = 3:
- Re-parameterize Rs identification (p0621 = 0, 1)
- Shut down quick magnetizing (p1401.6 = 0).