Forum

Share:
Notifications
Clear all

A07428 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
159 Views
Posts: 18018
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Technology controller parameterizing error comes when the technology controller has a parameterizing error.
Alarm value (r2124, interpret decimal): 1: The upper output limit in p2291 is set lower than the lower output limit in p2292.

Re alarm value = 1:
Set the output limit in p2291 higher than in p2292.
See also: p2291 (Technology controller maximum limiting), p2292 (Technology controller minimum limiting)

 

Share: