Cause : Torque/speed out of tolerance comes when the torque deviates from the torque/speed envelope characteristic for p2193 = 1.
For p2193 = 2 - The speed signal from the external encoder (refer to p3230) deviates from the speed (r2169).
- check the connection between the motor and load.
- adapt the parameterization corresponding to the load.