Cause : Enable signals for the rotating measurement missing comes when the rotating measurement cannot be started due to missing enable signals.
For p1959.13 = 1, the following applies:
- enable signals for the ramp-function generator missing (see p1140 ... p1142).
- enable signals for the speed controller integrator missing (see p1476, p1477).
- acknowledge faults that are present.
- establish missing enable signals.
See also: r0002 (Drive operating display), r0046 (Missing enable sig)