A08565 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
144 Views
Posts: 18023
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Consistency error affecting adjustable parameters comes when a consistency error was detected when activating the configuration (p8925 = 1) for the PROFINET interface. The currently set configuration has not been activated.

- IP address, subnet mask or default gateway is not correct
- IP address or station name used twice in the network
- station name contains invalid characters, etc

Check the required interface configuration (p8920 and following), correct if necessary, and activate (p8925 = 1). See also: p8925 (PN interface configuration)