A08757 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
199 Views
Posts: 18023
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Set COB-ID invalid comes when online operation, the appropriate COB-ID must be set invalid before mapping.

Example: Mapping for RPDO 1 should be changed (p8710[0]).
--> set p8700[0] = C00006E0 hex (invalid COB-ID)
--> set p8710[0] as required.
--> p8700[0] enter a valid COB-ID

Set the COB-ID to invalid.