Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
1,450
Views
Feb 16, 2024 4:58 am
Cause : Hardware current limiting in phase U comes when hardware current limit for phase U responded. The pulsing in this phase is inhibited for one pulse period.
- closed-loop control is incorrectly parameterized.
- fault in the motor or in the power cables.
- the power cables exceed the maximum permissible length.
- motor load too high.
- power unit defective.
- check the motor data and if required, recalculate the control parameters (p0340 = 3). As an alternative, run a motor data identification (p1910 = 1, p1960 = 1).
- check the motor circuit configuration (star/delta).
- check the motor load.
- check the power cable connections.
- check the length of the power cables.