A30032 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
220 Views
Posts: 18049
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Hardware current limiting in phase V comes when hardware current limit for phase V responded. The pulsing in this phase is inhibited for one pulse period.

- closed-loop control is incorrectly parameterized.
- fault in the motor or in the power cables.
- the power cables exceed the maximum permissible length.
- motor load too high
- power unit defective.

  1. Check the motor data and if required, recalculate the control parameters (p0340 = 3). As an alternative, run a motor data identification (p1910 = 1, p1960 = 1).
  2. check the motor circuit configuration (star/delta).
  3. check the motor load.
  4. check the power cable connections.
  5. check the power cables for short-circuit or ground fault.
  6. check the length of the power cables.