Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
212
Views
Feb 16, 2024 5:15 am
Cause : Line asymmetry comes when frequencies have been detected on the DC link voltage that would suggest line asymmetry or failure of a line phase. It is also possible that a motor phase has failed.
Fault F30011 is output if the alarm is present and at the latest after 5 minutes. The precise duration depends on the power unit type and the particular frequencies.
- check the line phase connection.
- check the motor feeder cable connections. If there is no phase failure of the line or motor, then line asymmetry is involved.
- reduce the power in order to avoid fault F30011.