A32915 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
153 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

cause : Configuration error comes when the configuration for encoder 2 is incorrect or Re-parameterization between fault/alarm is not permissible.

Alarm value (r2124, interpret decimal):

1: Re-parameterization between fault/alarm is not permissible.

419: When the fine resolution Gx_XIST2 is configured, the encoder identifies a maximum possible absolute position
actual value (r0483) that can no longer be represented within 32 bits.

Re alarm value = 1:
No re-parameterization between fault/alarm.

Re alarm value = 419:
Reduce the fine resolution (p0419) or deactivate the monitoring (p0437.25), if the complete multiturn range is not required.