Forum

Share:
Notifications
Clear all

A32940 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
116 Views
Posts: 18132
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

cause : Spindle sensor S1 voltage incorrect comes when the voltage of analog sensor S1 is outside the permissible range.

- Check the clamped tool.
- Check the tolerance and if required, adapt (p5040).
- Check the thresholds and if required, adapt (p5041).
- Check analog sensor S1 and connections.

Share: