A33161 alarm in siemens G120 Drive

1 Posts
1 Users
0 Reactions
208 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

cause : Analog sensor channel B failed comes when the input voltage of the analog sensor is outside the permissible limits.

Fault value (r0949, interpret decimal):

1: Input voltage outside detectable measuring range.
2: Input voltage outside the measuring range set in (p4675).
3: The absolute value of the input voltage has exceeded the range limit (p4676).

For fault value = 1:
- check the output voltage of the analog sensor.

For fault value = 2:
- check the voltage setting for each encoder period (p4675).