Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
92
Views
Feb 15, 2024 5:04 am
Cause : Defect in F-IO processing comes when cross checking and comparing the two monitoring channels, the drive detected a difference between parameters or results of the F-IO processing and initiated a STOP F. One of the monitoring functions no longer reliably functions - i.e. safe operation is no longer possible.
- The safety message C01711 with message value 0 is also displayed due to initiation of STOP F.
- If at least one monitoring function is active, then safety message C01701 "SI Motion: STOP B initiated" is output.
- check parameterization in the parameters involved and correct if required.
- ensure equality by copying the SI data to processor 2 and then carry out an acceptance test.