Forum

Share:
Notifications
Clear all

C01714 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
117 Views
Posts: 18038
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Safely-Limited Speed exceeded comes when the drive has moved faster than that specified by the velocity limit value (p9531). The drive is stopped as a result of the configured stop response (p9563).

- check the traversing/motion program in the control.
- check the limits for "Safely-Limited Speed (SLS) and if required, adapt (p9531)

Share: