Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
180
Views
Feb 16, 2024 6:59 am
Cause : Defect in a monitoring channel comes when cross-comparing the two monitoring channels, the drive detected a difference between the input data or results of the monitoring functions and initiated a STOP F. One of the monitoring functions no longer reliably functions - i.e. safe operation is no longer possible.
If at least one monitoring function is active, then message C30701 "SI Motion: STOP B initiated" is output.
- de-select encoderless monitoring functions, select and de-select STO.
- if monitoring function is active, issue "SLS" pulse enable within 5 s of de-selecting STO.