C30716 in siemens G120 Drive

1 Posts
1 Users
0 Reactions
125 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Tolerance for safe motion direction exceeded comes when the tolerance for the "safe motion direction" function was exceeded. The drive is stopped as a result of the configured stop response (p9366).

Message value (r9749, interpret decimal):

0: Tolerance for the "safe motion direction positive" function exceeded.
1: Tolerance for the "safe motion direction negative" function exceeded.

- check the traversing/motion program in the control.
- check the tolerance for "SDI" function and if required, adapt (p9364).

This message can be acknowledged as follows:

- Deselect the "SDI" function and select again.
- Perform a safe acknowledgment via F-DI or PROFIsafe